- Location
- Atlanta, GA US
The NEC 2011 250.64(C)(1) states that the grounding electrode conductor(s) shall be installed in one continuous length without a splice or joint. From the exception a splice shall be permitted either by irreversible compression-type connectors or by the exothermic welding process.
I have a main switchboard with a grounding electrode conductor from the main ground bus to a ground busbar adjacent to the equipment. From this busbar i then show the grounding electrode conductor attaching to the nearest water pipe as required by the NEC.
My question is at this busbar are the terminations required to be irreversible compression type/exothermically welded or can they be a standard listed bolt fitting as pictured below?
Code 250.64(F)(3) permits the use of listed connectors or an exothermic weld. (Picture below from Mike Holt's Grounding Vs Bonding Book page 94)
So it seems its acceptable however I'm confused if the 250.64(C) Continuous code supersedes 250.64(F)?
My goal is to make sure I either enforce an exothermic weld/compression fitting to the busbar or allow the much easier UL listed bolt.
I have a main switchboard with a grounding electrode conductor from the main ground bus to a ground busbar adjacent to the equipment. From this busbar i then show the grounding electrode conductor attaching to the nearest water pipe as required by the NEC.
My question is at this busbar are the terminations required to be irreversible compression type/exothermically welded or can they be a standard listed bolt fitting as pictured below?
Code 250.64(F)(3) permits the use of listed connectors or an exothermic weld. (Picture below from Mike Holt's Grounding Vs Bonding Book page 94)
So it seems its acceptable however I'm confused if the 250.64(C) Continuous code supersedes 250.64(F)?
My goal is to make sure I either enforce an exothermic weld/compression fitting to the busbar or allow the much easier UL listed bolt.