Continuous grounding electrode

kjroller

Member
Location
Dawson Mn
Occupation
Master electrician
(C) Continuous
Except as provided in 250.30(A)(5) and (A)(6), 250.30(B)(1), and 250.68(C), grounding electrode conductor(s) shall be installed in one continuous length without a splice or joint. If necessary, splices or connections shall be made as permitted in the following:
  1. Splicing of the wire-type grounding electrode conductor shall be permitted only by irreversible compression-type connectors listed as grounding and bonding equipment or by the exothermic welding process.
( I was gonna splice with irreversible crimp which is one of the ways permitted) however am I allowed to do so. Or does it have to meet one of the exceptions. For me to splice? Or can I splice anytime with irreversible crimp
 
So this is a GEC that you're splicing? If so it can be spliced with an irreversible type connector or cadwelded.

Welcome to the Forum. :)
 