If I have a 37amp continuous load conductor
sized to * 1.25 = 46.25
so I would use #6 rated at 55amps
But what about my ocpd
Would I take my load of 37 * 1.25 = 46.25
There in no breaker rated at 46.25 so I would use a 50amp breaker correct ?