continuous load

Status
Not open for further replies.

The electron man

Senior Member
Location
Nyc
Occupation
Electrician
If I have a 37amp continuous load conductor
sized to * 1.25 = 46.25

so I would use #6 rated at 55amps

But what about my ocpd

Would I take my load of 37 * 1.25 = 46.25

There in no breaker rated at 46.25 so I would use a 50amp breaker correct ?
 

infinity

Moderator
Staff member
Location
New Jersey
Occupation
Journeyman Electrician
What is the wiring method (conduit and wire, MC cable, NM cable, Etc.)? In the list I mentioned all but NM cable can be used as a 75° C conductor meaning that #8 AWG is sufficient for 50 amps.
 

The electron man

Senior Member
Location
Nyc
Occupation
Electrician
What is the wiring method (conduit and wire, MC cable, NM cable, Etc.)? In the list I mentioned all but NM cable can be used as a 75° C conductor meaning that #8 AWG is sufficient for 50 amps.
Don't we use the 60° column for anything under 100amps and its conduit and wire
 

HEYDOG

Senior Member
If I have a 37amp continuous load conductor
sized to * 1.25 = 46.25

so I would use #6 rated at 55amps

But what about my ocpd

Would I take my load of 37 * 1.25 = 46.25

There in no breaker rated at 46.25 so I would use a 50amp breaker correct ?
Yes! For Nonmetallic Sheathed Cable with a 60 degree C rating!
 

infinity

Moderator
Staff member
Location
New Jersey
Occupation
Journeyman Electrician
Don't we use the 60° column for anything under 100amps and its conduit and wire
Its thhn so what column would I use and was the calculation for my ocpd correct ?
THHN is 90° C conductor and can be used at its 75° C ampacity when the wiring method is conduit and wire. NM cable is limited to the 60° C ampacity due to 334.80.
 

wwhitney

Senior Member
Location
Berkeley, CA
Occupation
Retired
Don't we use the 60° column for anything under 100amps and its conduit and wire
Yes as a default if terminal ratings are unlabeled. But in practice most equipment terminals are rated for 75C wire. So if you are using a 75C wiring method (not NM, not LFNC or LFMC in a wet location), and you confirm that the terminals are labeled for 75C wire, you get to the use the 75C column, even under 100A.

And yes, you need a 50A breaker with conductor ampacity of at least 46A.

Cheers, Wayne
 