So after conductor ampacity adjustment/corrections for a continuous load you don't need to use 125% of the load but only a 100%?
 
Yes, that's correct

Find the conductor size needed for 100% of the non-continuous load plus 125% of the continuous load (without any adjustments/corrections).

Then find the conductor size needed for 100% of the non-continuous load plus 100% of the continuous load, after any adjustments/corrections.

The larger size conductor is required.

Note, also, that the ampacity of the conductor after any adjustments/corrections must be properly protected per Art. 240.
 