madpenguin
Member
I'm a little confused here and know you guys can help me out... :wink:
I've been told several times that continuous load circuits need to be at 80% of the OCPD. That means:
15A = 12A
20A = 16A
30A = 24A
But the NEC tells me not to calculate by OCPD but by 125% of the actual load. Which is it because they don't compliment one another.
I'm going to install 4 - 5' baseboard heaters in my attic @ 240v. I'm using 10/2 on a 30A DP breaker.
250w per linear foot = 5000w draw
5000w/240v = 20.83A
20.83A x 1.25 = 26.038A
24A != 26.038A
I think I must be missing something here. The first method tells me I'm over. The second method tells me I have room to spare.....
Thanks!