215.2(A)(1) is confusing the heck out of me:
"The minimum feeder conductor size, before application of any adjustment or correction factors, shall have an allowable ampacity not less than the noncontinuous load plus 125% of the continuous load."
This only applies to the feeder conductors, not the circuit breaker. Is there a similar requirement that the circuit breaker has to be sized for 125% of the continuous load? I thought there was, but I cant find it in 240.
Steve