I have a job where there will be at least 3 sub-panels being fed from a 400-320 amp 240 v 1 phase meter center. It has a G.E. meter assembly with a 200 A breaker feeding a 8 circuit load center with bottom lugs for feed through and an empty space for a 2nd breaker not yet installed with a conduit chase to feed future loads.
So far, the loads calculate out to 180 amps to 2 load centers using using optional load calculations, 220 A standard calculations. There will be future loads such as swimming pool and car chargers coming p on next revision, which is why we chose 400 / 320 A meter center.
I understand that the entire service can utilize the optional load calc for a total load, but I am wondering if there is a list of items that is considered a continuous load that must be calculated at 125% continuous load, and since eventually there will be at least 3-4 load centers fed by the 2 200 A breakers,
must all panel feeds need to be calculated at 100% and 125% depending on whether they are continuous loads ?
thanx, dhsvcs
So far, the loads calculate out to 180 amps to 2 load centers using using optional load calculations, 220 A standard calculations. There will be future loads such as swimming pool and car chargers coming p on next revision, which is why we chose 400 / 320 A meter center.
I understand that the entire service can utilize the optional load calc for a total load, but I am wondering if there is a list of items that is considered a continuous load that must be calculated at 125% continuous load, and since eventually there will be at least 3-4 load centers fed by the 2 200 A breakers,