Continuous Loads

Status
Not open for further replies.
Can continuous loads be derated as per table 220.11, table 220.13, 220.18, 220.19, 220.20, 220.32 and if not what article(s) tells us not to?
 

bennie

Esteemed Member
Re: Continuous Loads

A load is never derated. The load numbers are increased when calculating for over 3 hours of in use continously.

The ampacity of a conductor is reduced to reflect the increase in load as per calculation.

To determine wire size, add 25% to the actual connected load.

To determine permitted load, deduct 20% from the ampacity of the conductor.
 