So I have been trying to come up with evidence to support my side of a design with my PE.
System information
60kw PV system name plate rating at 208V is equal to 166A, Due to it being a PV system, it needs to be corrected for continuous use. This means the corrected current rating is 208A. I am using a 225A Breaker and Enclosure for the primary OCPD. However when it comes to the Disconnect Device (705.22) I am trying to show that a 200A 100% rated switch can be used and not be in violation of code. My PE is under the assumption that because it is a continuous duty system that the output conductors have to be corrected for the 1.25 correction factor and that amperage must be the sizing factor. Which I agree with and wholeheartedly understand. I would agree that if the disconnect was only rated for 80% that I would have to use a 400A switch to comply with code. My argument is that a 100% rated switch has been tested and rated to take up to its name plate rating without the need for a correction factor, the switch has been tested for the additional heat and so on that it would experience at full load continuously.
I know ultimately it is his stamp, and the AHJ has final word. I am trying to save the cost and eye sore of installing a 400A switch when it can be accomplished with a 200A switch legally.
Please correct me if i'm wrong, but also direct me to where I can show that this is correct.
Thank you.
System information
60kw PV system name plate rating at 208V is equal to 166A, Due to it being a PV system, it needs to be corrected for continuous use. This means the corrected current rating is 208A. I am using a 225A Breaker and Enclosure for the primary OCPD. However when it comes to the Disconnect Device (705.22) I am trying to show that a 200A 100% rated switch can be used and not be in violation of code. My PE is under the assumption that because it is a continuous duty system that the output conductors have to be corrected for the 1.25 correction factor and that amperage must be the sizing factor. Which I agree with and wholeheartedly understand. I would agree that if the disconnect was only rated for 80% that I would have to use a 400A switch to comply with code. My argument is that a 100% rated switch has been tested and rated to take up to its name plate rating without the need for a correction factor, the switch has been tested for the additional heat and so on that it would experience at full load continuously.
I know ultimately it is his stamp, and the AHJ has final word. I am trying to save the cost and eye sore of installing a 400A switch when it can be accomplished with a 200A switch legally.
Please correct me if i'm wrong, but also direct me to where I can show that this is correct.
Thank you.