Good day all, while sizing a generator for a building at one of our facilities I installed our Amprobe DMII pro to log loads. Later when analyzing the data I noticed spikes that were traced back to this compressor that ran upwards of 340 amps @ 208. Running amps about 36. My cure for greatly reducing the size of the generator would be convert the compressor to constant run and running it with the unloader like they do in industrial situations. This facility uses a lot of air and the machine cycles on 2 minutes off 2 minutes with a 40 psi differential. Opinions on compressor life versus cost of constant run would be greatly appreciated.. Long time lurker, first time poster Thanks, Scott