Is the door with electrical components installed on it required to be grounded? If so, what code section requires this?


Dave
 
It may not be NEC application, but rather a UL508A. But 508A requires the door to be bonded if there are powered devices on the door.
 
Likewise, if the installation is subject to NFPA 79 then article 8.2.3.6.1 of that standard applies:

"Where electrical devices are mounted on conductive
doors or covers, an equipment (protective) bonding jumper
shall be installed."
 