Hello all,
I would like an opinion on the case below.
The engineer plans were basically an 800A main disconnect service - connected to a gutter 12"x12"x14' - and separate disconnects to each building (200A each with their own meter) for a total of (5 disconnects).
The contractor trying to save time on gear and cost revised into - main feeder conduit going straight to the gutter 12"x12"x14' and separate disconnects to each building (200A each with their own meter) for a total of (5 disconnects). So he removed the main disconnect and went straight to the gutter.
In my opinion both designs work and code compliant (unless you see something i don't). Would you accept something like that from personal experience?? or say to follow the original design.
Thank you
I would like an opinion on the case below.
The engineer plans were basically an 800A main disconnect service - connected to a gutter 12"x12"x14' - and separate disconnects to each building (200A each with their own meter) for a total of (5 disconnects).
The contractor trying to save time on gear and cost revised into - main feeder conduit going straight to the gutter 12"x12"x14' and separate disconnects to each building (200A each with their own meter) for a total of (5 disconnects). So he removed the main disconnect and went straight to the gutter.