Hi all,
I've received a ton of great information here, but there's one thing I've looked for endlessly that I just can't quite wrap my head around at this point, so perhaps someone could help me out.
We are installing a service in a commercial building, so to get an accurate readings of the machines continuous amp draw, I put my clamp meter on the machines, and read a running current of 25 amps per phase at 480v 3 phase, balanced across A B and C
I understand a 25 amp 3 phase loads draw 25 amps per phase, and to convert to KVa Im using S(kVA) = √3 × I(A) × VL-L(V) / 1000 where V =480 and I =25 which puts me at about 20.785 kva. So the contractor provided me a panel schedule the reflected 20.785/3 which equals about 6928 VA and put that in each of the phases. So A = 6928 va B= 6928 va c=6928va.
So here is where Im questioning the calculation, we have (3) of the same machines. So from a logic standpoint I would say 25 amps per phase for one machine should give me around 75 amps per phase for all 3 connected. 75 amps on A, 75 amps on B, and 75 on C.
What he is doing is adding the 6928 (3) times to add up the VA per phase for all (3) machines to get 20785 va per phase on A B and C, then calculated each individual phases current draw using the calculation I(A) = 1000 × S(kVA) / (√3 × VL-L(V) ) where V=480 and S = 20.785.
Notice the 3 phase calculation .
That gave him a calculation of 26 amps per phase. Wouldn't he have to use a single phase calculation if he is just going to add up the VA values from each of the phases and calculate them individually?
So shouldn't he be calculating these at single phase 277 volts to get the current draw per Phase? Or am I missing something here?
Thanks In advance!
Scott
I've received a ton of great information here, but there's one thing I've looked for endlessly that I just can't quite wrap my head around at this point, so perhaps someone could help me out.
We are installing a service in a commercial building, so to get an accurate readings of the machines continuous amp draw, I put my clamp meter on the machines, and read a running current of 25 amps per phase at 480v 3 phase, balanced across A B and C
I understand a 25 amp 3 phase loads draw 25 amps per phase, and to convert to KVa Im using S(kVA) = √3 × I(A) × VL-L(V) / 1000 where V =480 and I =25 which puts me at about 20.785 kva. So the contractor provided me a panel schedule the reflected 20.785/3 which equals about 6928 VA and put that in each of the phases. So A = 6928 va B= 6928 va c=6928va.
So here is where Im questioning the calculation, we have (3) of the same machines. So from a logic standpoint I would say 25 amps per phase for one machine should give me around 75 amps per phase for all 3 connected. 75 amps on A, 75 amps on B, and 75 on C.
What he is doing is adding the 6928 (3) times to add up the VA per phase for all (3) machines to get 20785 va per phase on A B and C, then calculated each individual phases current draw using the calculation I(A) = 1000 × S(kVA) / (√3 × VL-L(V) ) where V=480 and S = 20.785.
Notice the 3 phase calculation .
That gave him a calculation of 26 amps per phase. Wouldn't he have to use a single phase calculation if he is just going to add up the VA values from each of the phases and calculate them individually?
So shouldn't he be calculating these at single phase 277 volts to get the current draw per Phase? Or am I missing something here?
Thanks In advance!