Control and Power cable separation...

Status
Not open for further replies.

scadaman

Member
What is a good rule of thumb for separation of a 4-20mA analog signal from 480V power cable? I have a location where we need to run both overhead on the same poles. The NEC just gives minimum (safety) distances...I am concerned with crosstalk--we are runnning shielded, armored cable, and I am looking for a "safe" parallel distance (could put one 6" below the other, for example)

Thanks
 

stickelec

Senior Member
Since both are "Armored and Shielded", and if properly grounded, I don't see a noise problem on the Analog cable. No different then running them in separate RGC or EMT.
 