My question likely touches on some areas of the NEC, but I'm asking it in the General Electrical forum since it seems to relate more particularly to NFPA 79, specifically, section 7.2.4, Control Circuit Protection.
What does the code (7.2.4.2.2) mean when it states, "Control circuit conductors sizes of 18, 16, and 14 AWG shall be considered as protected by an overcurrent devices(s) of not more than a 20-ampere rating." Does this mean that I should use over-current protection, or does the phrase, "shall be considered as protected" mean that my control circuit may actually go without protection so long as it does not draw more than 20 amps?
I suspect that the former is the right interpretation, i.e. I should use fuses (or MCBs) that do not exceed a 20-amp rating if I happen to be using 14 AWG wire.
However, that raises the question in my mind as to why someone wrote 7.2.4.2.2 in the first place. In light of section 12.5 of NFPA 79, what is the justification for using protection rated up to 20 amps on, say, an 18 AWG wire, which is otherwise not rated for more than 7 amps? One may wonder whether the assumption is that in a control circuit, the likelihood of reaching 7 amps is considered to be almost nil. For this reason I ask whether I am properly interpreting this section.
By way of background, what leads to this question is my inclusion of a phase- and voltage-monitoring relay device in an industrial panel fed by a 480 Wye Mains supplying (probably) over 100 amps. The panel distributes power to numerous branch circuits located in the panel. The relay device would be installed on the load-side of a suitably-sized Mains circuit breaker before the separation into the several branches. The phase-monitoring relay documentation says that the device itself requires no fusing, but that "fusing for the line protection depends on the cross-section used." The device is made to support wires of 20 to 14 AWG, so my monitoring relay connect to the panel mains through a set of terminal blocks.
Since the relay is used to monitor rather than deliver the 3-phase power, I presume that it and its feeding conductors a control circuit, not part of the power circuit. Please correct me if this presupposition is in error. If I am correct, however, then section 7.2.4.2 applies.
Best regards,
The Shackled Designer
My question likely touches on some areas of the NEC, but I'm asking it in the General Electrical forum since it seems to relate more particularly to NFPA 79, specifically, section 7.2.4, Control Circuit Protection.
What does the code (7.2.4.2.2) mean when it states, "Control circuit conductors sizes of 18, 16, and 14 AWG shall be considered as protected by an overcurrent devices(s) of not more than a 20-ampere rating." Does this mean that I should use over-current protection, or does the phrase, "shall be considered as protected" mean that my control circuit may actually go without protection so long as it does not draw more than 20 amps?
I suspect that the former is the right interpretation, i.e. I should use fuses (or MCBs) that do not exceed a 20-amp rating if I happen to be using 14 AWG wire.
However, that raises the question in my mind as to why someone wrote 7.2.4.2.2 in the first place. In light of section 12.5 of NFPA 79, what is the justification for using protection rated up to 20 amps on, say, an 18 AWG wire, which is otherwise not rated for more than 7 amps? One may wonder whether the assumption is that in a control circuit, the likelihood of reaching 7 amps is considered to be almost nil. For this reason I ask whether I am properly interpreting this section.
By way of background, what leads to this question is my inclusion of a phase- and voltage-monitoring relay device in an industrial panel fed by a 480 Wye Mains supplying (probably) over 100 amps. The panel distributes power to numerous branch circuits located in the panel. The relay device would be installed on the load-side of a suitably-sized Mains circuit breaker before the separation into the several branches. The phase-monitoring relay documentation says that the device itself requires no fusing, but that "fusing for the line protection depends on the cross-section used." The device is made to support wires of 20 to 14 AWG, so my monitoring relay connect to the panel mains through a set of terminal blocks.
Since the relay is used to monitor rather than deliver the 3-phase power, I presume that it and its feeding conductors a control circuit, not part of the power circuit. Please correct me if this presupposition is in error. If I am correct, however, then section 7.2.4.2 applies.
Best regards,
The Shackled Designer