Good morning,
I think I have this one squared away, but want to "check-in" anyways.
Working with a customer that would like to have a light for trip/overload indication. In a combo motor starter this is easy to accomplish considering we tap off the load side of the breaker for the control circuit, and then use the alarm contact on the overload relay to provide indication. During an overload, the control circuit is still live, and we can power the indicating light.
Now, we have feeder breakers we are also providing. Customer is requesting that we provide indication for breaker trip. They're requesting a CPT within the enclosure to power the indicating light. Note that these are 3P 480V breakers, and 480-120 CPT are being used throughout. We initially stated that customer will need to provide external power to feed the indicating light since the 120V control circuit will de-energize when the breaker trips. They came back and said to tap off the load side of the breaker. My issue here is the load side conductors are taps, and per 240.21 you "can't tap a tap."
Is my reasoning sound here? If the load side conductors were feeders I wouldn't have an issue, but they're not...
If I am right, does anyone have any other ideas in terms of how an indicating light can be powered within an enclosure without an external source, with a breaker that is being fed by tap conductors? Doesn't seem like there are any other options aside from feeding it from an external source...
Thanks in advance, hope my explanation isn't confusing.
I think I have this one squared away, but want to "check-in" anyways.
Working with a customer that would like to have a light for trip/overload indication. In a combo motor starter this is easy to accomplish considering we tap off the load side of the breaker for the control circuit, and then use the alarm contact on the overload relay to provide indication. During an overload, the control circuit is still live, and we can power the indicating light.
Now, we have feeder breakers we are also providing. Customer is requesting that we provide indication for breaker trip. They're requesting a CPT within the enclosure to power the indicating light. Note that these are 3P 480V breakers, and 480-120 CPT are being used throughout. We initially stated that customer will need to provide external power to feed the indicating light since the 120V control circuit will de-energize when the breaker trips. They came back and said to tap off the load side of the breaker. My issue here is the load side conductors are taps, and per 240.21 you "can't tap a tap."
Is my reasoning sound here? If the load side conductors were feeders I wouldn't have an issue, but they're not...
If I am right, does anyone have any other ideas in terms of how an indicating light can be powered within an enclosure without an external source, with a breaker that is being fed by tap conductors? Doesn't seem like there are any other options aside from feeding it from an external source...
Thanks in advance, hope my explanation isn't confusing.