A design has been proposed to use an autotransformer to produce 120VAC control voltage in a commercial clothes dryer.
NFPA 79 electrical standards for industrial machinery article 9.2 (control circuit voltages) this limits controls to 120VAC.
Is it true that this 120VAC must not be derived from an autotransformer?
Was the following incorporated into article 9.2?
"9.1.1.1 Control transformers shall be used for supplying the control
circuits. Control circuits shall not be derived from autotransformers."
Thanks and best wishes in the New Year