Control Panel FLC Require 125%

Ravenvalor

Senior Member
Location
Triad region of NC
Occupation
Electrician
Hello,

I have a customer with a control panel that has a sticker on the front that says 85.1 FLC.

The components that it feeds have already had the 25% calculated for the conductors and the fuses that are being fed by the control panel.

I was wondering, do I have to add another 25% to the 85.1-amps when calculating the breaker size and the conductor size?

This would put the breaker size at 110amps. Or can I just use a 90-amp breaker with conductors rated 90-amp?


Thank you for your assistance.
 