Hello,
I have a customer with a control panel that has a sticker on the front that says 85.1 FLC.
The components that it feeds have already had the 25% calculated for the conductors and the fuses that are being fed by the control panel.
I was wondering, do I have to add another 25% to the 85.1-amps when calculating the breaker size and the conductor size?
This would put the breaker size at 110amps. Or can I just use a 90-amp breaker with conductors rated 90-amp?
Thank you for your assistance.