Hello,

Is it typical to house VFD in an external enclosure for Nema 1 or IP21 rated VFDs? I've got control relays and some reset PBs that I need to locate in a control panel in addition to control transformer. It sounds like putting the VFD and aux. devices in a control panel/enclosure makes sense and provides additional protection.

Thanks,
EE
 
Make sure there is sufficient ventilation is main thing.

Doesn't necessarily need to be a powered vent, but if you trap too much heat in your enclosure drive will trip on high temp limit.
 
Hello,

Is it typical to house VFD in an external enclosure for Nema 1 or IP21 rated VFDs? I've got control relays and some reset PBs that I need to locate in a control panel in addition to control transformer. It sounds like putting the VFD and aux. devices in a control panel/enclosure makes sense and provides additional protection.

Thanks,
EE

very typical.
 