Hi
We are using an NEMA 4 control panel in a plant process area that until reasently had General Purpose Area Classification.
Since you call it a control panel, it brings up another question. What are you doing with your protruding devices, controls that are located on the panel surface? They are exposed to the hazardous environment and must be replaced or protected. A pushbutton is probably not an issue, anything else should be reviewed. Panel meters and single loop controllers are suspect. Pilot lights may or may not be OK.
Devices protruding thru the enclosure - Logically one wants to make them acceptable for the area classification that they are exposed to. If the enclosure is unclassified inside, the enclosure wall is the boundary and the area outside of it is hazardous. There is no magic force field that envleopes the protruding devices.
Review the commentary in the NEC Handbook following 500.7(D). Key words "within the enclosure". The commentary goes on to mention pushbuttons and pilot lights being protected as long as their terminals are within the protected enclosure
Review the definitions in NFPA 496 for pressurization types. Key words "within the protected enclosure?
The following are excerpts from ISA-RP12.4-1996:
?Chapter 6 - Components that protrude through the enclosure? ?Components should permit the flow of the protective gas to properly purge and pressurize the component. (Additional information is located in Annex B.) Exception: components that are suitable for the hazardous location that would exist in the absence of the protective gas do not require purging or pressurization? ?Annex B, 6 ? This requirement is intended for components such as switches, keyboards, lamps, indicators, and for mechanical devices such as shafts that penetrate the enclosure. Methods of protection to comply with the exception include mounting the component in an explosion proof housing or using the component in an intrinsically safe circuit??
From P&F BEBCO EPS, Purging Technology Review:
The use of devices that penetrate the surface of a protected
enclosure must be carefully scrutinized. Protruding devices
will likely contain electrical components that could either be
exposed to the hazardous location or be isolated from the
fl ow of protective gas. Conventional wisdom suggests that a
protruding device should be acceptable if it is (1) explosion
proof, (2) intrinsically safe, (3) proven to emit insufficient energy
to ignite the surrounding atmosphere (applicable for Division 2
locations only), (4) constructed so that all electronics within its
face are suitably sealed from the surrounding environment and
properly ventilated to the protected enclosure, or (5) isolated
from the surrounding atmosphere by a sealed window or access
door that is properly ventilated to the protected enclosure.
Controllers, Indicators & Recorders
Today's panel mounted instrumentation is almost strictly
electronic. The protruding face of these instruments normally
contains LEDs, LCDs and incandescent or fl orescent lights.
Therefore, it is extremely important to isolate all instrumentation
from the surrounding atmosphere, unless the face is sealed
and all electronics are properly ventilated to the protected
enclosure.