sndbodkin
Member
- Location
- Blackfoot, Id
We installed a waste water lift station control panel. The panel has a 60 amp disconnect and controls two 240 vac 1 phase motors. The power is supplied to the control panel by a 100 amp 1 phase 240 vac breaker panel. The branch conductors feeding the control panel are 6 cu awg and are fed through a 60 amp 2 pole breaker. They neutral size is 12 awg. The neutral load in the control panel is milliamps that only connects to a 2.5 amp 24 vdc power supply.
The local inspector tells me that I need a neutral conductor capable of caring 60 amps to this panel based on 220.61a.
We have built and installed hundreds of control panels and we have never had an inspector require this.
The local inspector tells me that I need a neutral conductor capable of caring 60 amps to this panel based on 220.61a.
We have built and installed hundreds of control panels and we have never had an inspector require this.