juicethief
Member
- Location
- United States
I have been reviewing a design for an electric duct heater and the vendor schematic for the SCR controller shows two control transformers (480/120V - 200VA & 480/24V - 50VA, Class 2?). Both control transformers receive their supply from the load side of a manual disconnect supplied with the controller. The controller is being fed from an MCC cubicle with 35A fuses. However, there is no fusing in the primary of either control xfmr. There is a 3A fuse in the secondary of the 480/120V control xfmr and no fusing in the secondary of the 480/24V control xfmr. The control xfmr primary & secondary wiring is #14 & #18 for the 480/120V. The primary and secondary wiring is #18 for 480/24V.
My questions are: do control panels have to follow NEC rules and, if not, how can these be installed seemingly unprotected?
I would think this would need to conform with 450.3(B).
The panel is UL listed and none of the control wiring leaves the enclosure if that makes a difference.
My questions are: do control panels have to follow NEC rules and, if not, how can these be installed seemingly unprotected?
I would think this would need to conform with 450.3(B).
The panel is UL listed and none of the control wiring leaves the enclosure if that makes a difference.