The Problem: I have two (2) panels at two (2) different locations that are giving me roughly the same problems.
In both panels, the Processors have had major faults of various kinds. Most of them recoverable.
However, in one case, the processor was "bricked" and PLC power supply needed replaced.
The Information:
One panel is in Canada using 600V and the other is US using 480V.
They both use RA Compactlogix 1769-L33ER processors with PB4 power supplies.
The basic setup is the 480, or 600, steps down (ahead of disconnect) via TX to a UPS at 120. The UPS powers the 24VDC supply.
The 24VDC also powers the 1769-PB4 for the processor/PLC backplane.
Each power level is used for other things, but this is the basic structure.
During a recent storm, the Canadian panel blew a fast acting glass fuse on the 24V supplying Contactor Coils (Rockwell EJ Electronic coils) to a bunch of fans.
The processor also had a "backplane timout error". But it was recoverable.
The contactors shouldn't have changed state until the processor de-energized the outputs on Fault.
But the processor shouldn't have faulted because it is behind the UPS, 24V supply, and PB4 supply.
The Aha Moment:
What we just figured out is that both panels, at their locations, are wired closest to the switch gear. Meaning the shortest cable.
So, my only thought is the Grounding.
We do ground the TX, UPS, and 24V common.
Because these panels are closest, electrically, to the switch gear room, maybe these panels are absorbing grounding disruptions?
Does anyone have advice on how to mitigate this problem?
Or maybe i'm looking in the wrong place?
In both panels, the Processors have had major faults of various kinds. Most of them recoverable.
However, in one case, the processor was "bricked" and PLC power supply needed replaced.
The Information:
One panel is in Canada using 600V and the other is US using 480V.
They both use RA Compactlogix 1769-L33ER processors with PB4 power supplies.
The basic setup is the 480, or 600, steps down (ahead of disconnect) via TX to a UPS at 120. The UPS powers the 24VDC supply.
The 24VDC also powers the 1769-PB4 for the processor/PLC backplane.
Each power level is used for other things, but this is the basic structure.
During a recent storm, the Canadian panel blew a fast acting glass fuse on the 24V supplying Contactor Coils (Rockwell EJ Electronic coils) to a bunch of fans.
The processor also had a "backplane timout error". But it was recoverable.
The contactors shouldn't have changed state until the processor de-energized the outputs on Fault.
But the processor shouldn't have faulted because it is behind the UPS, 24V supply, and PB4 supply.
The Aha Moment:
What we just figured out is that both panels, at their locations, are wired closest to the switch gear. Meaning the shortest cable.
So, my only thought is the Grounding.
We do ground the TX, UPS, and 24V common.
Because these panels are closest, electrically, to the switch gear room, maybe these panels are absorbing grounding disruptions?
Does anyone have advice on how to mitigate this problem?
Or maybe i'm looking in the wrong place?