control power for Emergency Generators

Status
Not open for further replies.

mshields

Senior Member
Location
Boston, MA
I've inherited a project where my predecessor provide optional standby 120V control for the various components of a typical emergency generator that needs 120V power; jacket water heater, battery charger, lights, etc.

I would normally put these things a circuit fed to the generator from the Emergency Branch.

Are they required to be on Emergency Power per the NEC OR can I live with OS power for these things.
 

dkidd

Senior Member
Location
here
Occupation
PE
Lights should be on emergency power. The jacket heater isn't needed when it runs. If the generator has a battery charging alternator, the charger can be on normal power.
 

texie

Senior Member
Location
Fort Collins, Colorado
Occupation
Electrician, Contractor, Inspector
I've inherited a project where my predecessor provide optional standby 120V control for the various components of a typical emergency generator that needs 120V power; jacket water heater, battery charger, lights, etc.

I would normally put these things a circuit fed to the generator from the Emergency Branch.

Are they required to be on Emergency Power per the NEC OR can I live with OS power for these things.
You need to look at NFPA 110 for this.
 