Hello All,
I am looking for a control power load calculator (spreadsheet) developed for switchgear control power sizing to ensure the CPT and UPS ARE adequately sized. Any manufacturer spreadsheet would do I can modify the parameters.
I think you're just going to have to add up the maximum amount of power required at the same time. My suspicion is that for the most part it will just be adding up the VA required by each individual device which you should be able to do fairly easily with the sum function as mention by a previous poster.
There may be some cases where some devices can never be energized at the same time so you might be able to reduce your control power requirements slightly by eliminating the non simultaneous devices but probably it won't make much difference cost-wise and you never know what somebody is going to do down the road.
Most of the time when this is an issue it has to do with the DC backup system and how much battery power you need which can get a little pricey but that's just the way it is. I would not be trying to save money on batteries. You might get away with it for a while but you could also get burned pretty bad if you have a blackout and can't restart because your battery capacity is just a hair low