CobyRupert
Member
- Location
- NY
I'm having a argument w/ myself and need a 3rd opinion. 
If control room doors have an "airlock configuration" (i.e. 2 doors in series, with a vestibule area between the control room and Cl.1 Div 2 area), do you have to test air flow with both doors open?
We have a control room surrounded by a Cl. 1 Div 2 hazardous area. We will use a HVAC unit to supply Type Z pressurization to the Control Room to make it unclassified.
As per NFPA 496, Chapter 7.4 I understand the requirements to be:
(1) Maintain 25 Pa (.1" H2O) in control room with opening closed.
(2) Provide air flow of 60 ft/min "through all openings capable of being opened. The velocity shall be measured with all these openings simultaneously open, and a drop in pressure below the 25 Pa (.1 " H2O) specified in (1) shall be permitted while meeting this requirement."
The owner has an expectation that the control room will be entered through an airlock (but not really a "lock", i.e. no interlocks prevent both set of doors to be opened simultaneously. More like 2 doors in series with each other with a vestibule chamber area in between the doors)
Questions:
1. When we do the airflow 60ft/min test, as per requirement (2) do we have to have both set of airlock doors open?
- On one hand one could expect the answer to be "yes" because:
- On the other hand, would the answer still be "yes" if the "airlock chamber" was 20' long? (30 ft long? a 50' corridor, 4500 sq. ft? ...etc...? See where I'm going? i.e. where's the cutoff line?).
-Also when strictly reading item (2), isn't the control room "opening" only the first set of doors into the airlock, whereas the second set of doors (between the air lock and Cl. I Div 2 area) is not technically an opening for the pressurized area (control room)?
Perhaps the real question is: Is there any point to have an air lock? (Other than the HVAC doesn't have to cycle as much (i.e the room isn't "depressurized" as much when the control room door is opened.))
If control room doors have an "airlock configuration" (i.e. 2 doors in series, with a vestibule area between the control room and Cl.1 Div 2 area), do you have to test air flow with both doors open?
We have a control room surrounded by a Cl. 1 Div 2 hazardous area. We will use a HVAC unit to supply Type Z pressurization to the Control Room to make it unclassified.
As per NFPA 496, Chapter 7.4 I understand the requirements to be:
(1) Maintain 25 Pa (.1" H2O) in control room with opening closed.
(2) Provide air flow of 60 ft/min "through all openings capable of being opened. The velocity shall be measured with all these openings simultaneously open, and a drop in pressure below the 25 Pa (.1 " H2O) specified in (1) shall be permitted while meeting this requirement."
The owner has an expectation that the control room will be entered through an airlock (but not really a "lock", i.e. no interlocks prevent both set of doors to be opened simultaneously. More like 2 doors in series with each other with a vestibule chamber area in between the doors)
Questions:
1. When we do the airflow 60ft/min test, as per requirement (2) do we have to have both set of airlock doors open?
- On one hand one could expect the answer to be "yes" because:
- There is no interlock lock between the doors, i.e. both could be open at the same time? , and
- How would one get 60ft/min flow into the airlock vestibule if the second door is closed?
- On the other hand, would the answer still be "yes" if the "airlock chamber" was 20' long? (30 ft long? a 50' corridor, 4500 sq. ft? ...etc...? See where I'm going? i.e. where's the cutoff line?).
-Also when strictly reading item (2), isn't the control room "opening" only the first set of doors into the airlock, whereas the second set of doors (between the air lock and Cl. I Div 2 area) is not technically an opening for the pressurized area (control room)?
Perhaps the real question is: Is there any point to have an air lock? (Other than the HVAC doesn't have to cycle as much (i.e the room isn't "depressurized" as much when the control room door is opened.))