Control transformer in reverse

Status
Not open for further replies.

Sierrasparky

Senior Member
Location
USA
Occupation
Electrician ,contractor
I was approached to use a doorbell type 120v to 24v transformer in reverse to power a 120 volt trouble light fed from a 24v control circuit.
I said it was hokey and not proper listed use of the transformer.
 

drcampbell

Senior Member
Location
The Motor City, Michigan USA
Occupation
Registered Professional Engineer
There's nothing inherently wrong with using a transformer in reverse, although derating is sometimes required.

Three questions come to mind:
Most doorbell transformers are only capable of ~20 VA. Will that be sufficient?
Does the 24-volt circuit have enough spare capacity?
How is it that you have a 24-volt AC circuit available, but not a 120-volt circuit?
 

Sierrasparky

Senior Member
Location
USA
Occupation
Electrician ,contractor
There's nothing inherently wrong with using a transformer in reverse, although derating is sometimes required.

Three questions come to mind:
Most doorbell transformers are only capable of ~20 VA. Will that be sufficient?
Does the 24-volt circuit have enough spare capacity?
How is it that you have a 24-volt AC circuit available, but not a 120-volt circuit?

Yes, runs only .05ma.

Reason for request : Trouble light wire was CL2 Lo VO wire run in same conduit as other Power limited cable. The suggestion is to be able to re-use the status/strobe light.
 

sameguy

Senior Member
Location
New York
Occupation
Master Elec./JW retired
Look at Acme xformers web site they show you how to size machine tool xfmrs in reverse 1kv and less I believe.
 

GoldDigger

Moderator
Staff member
Location
Placerville, CA, USA
Occupation
Retired PV System Designer
It's 0.06 VA based on his revised current.
But I'm with you. Is that useful for a light of any sort?
Here in the US we use "trouble light" in two different senses:
1. A temporary with a cage shield and/or reflector light on a long cord used as a portable worklight, or
2. An indicator light showing that there is a problem.
.06VA would not do much for 1, but might be fine for 2.
Also, .5A instead of .5mA gives a much more believable result for 1.

Sent from my XT1585 using Tapatalk
 

Sierrasparky

Senior Member
Location
USA
Occupation
Electrician ,contractor
How are you calculating the available current in a reverse transformer? I don't get what you folks get.
 

LarryFine

Master Electrician Electric Contractor Richmond VA
Location
Henrico County, VA
Occupation
Electrical Contractor
Correctamundo! a = va/v = 20/120 = 0.166 @ 120v = 0.833a @ 24v. (presuming 100% efficiency).

If you think about it, all we acare about is the power; a 20va transformer will just light up a 20w bulb.

I found several 24v/75va HVAC transformers in the $35 range. Should obviously give you about 75w.
 