Control Transformer voltage Question.

Status
Not open for further replies.

Mporter4

Member
I am building a plc cabinet with starters,p/b, pilot lights etc.
I was going to purchase a 480v primary 240/120 secondary (2000va) enclosed.I was talking to a co-worker and he said by only using one leg of the 240v would make this an unbalanced system.
I think this would be correct but to purchase a 480v to 120v control transformer is going to run me about a $950.00.(SOLA HZ-122000) would I be okay with the 240/120 secondary??:eek:
 

jim dungar

Moderator
Staff member
Location
Wisconsin
Occupation
PE (Retired) - Power Systems
It all depends on your transformer and your loading.

Your transformer is not going to be affected by a '100%' unbalance. However a 2000VA 120/240V transformer is rated for 8.33A per winding, which would mean you would only be able to supply 8.33 x 120 = 1000VA of load.

Many transformers are re-connectable, for 100% loading, as 120V 2wire, 240V 2wire, or 120/240V 3wire.
 
Last edited:

ATSman

ATSman
Location
San Francisco Bay Area
Occupation
Electrical Engineer/ Electrical Testing & Controls
I am building a plc cabinet with starters,p/b, pilot lights etc.
I was going to purchase a 480v primary 240/120 secondary (2000va) enclosed.I was talking to a co-worker and he said by only using one leg of the 240v would make this an unbalanced system.
I think this would be correct but to purchase a 480v to 120v control transformer is going to run me about a $950.00.(SOLA HZ-122000) would I be okay with the 240/120 secondary??:eek:

Normally if you parallel the 2 secondary windings to feed the 120V load (instead of a series configuration for 240V) then you utilize the full 2KVA capacity of the transformer.
 

SG-1

Senior Member
Do you have a model number for the transformer you want to use ? The second ( Sola ) transformer has an 80 degree C temperature rise. The transformer is mounted outside of the control box ?
 

Jraef

Moderator, OTD
Staff member
Location
San Francisco Bay Area, CA, USA
Occupation
Electrical Engineer
If the "enclosed" transformer means it is a distribution transformer, you will need a larger transformer for the same task as a Control Power Transformer. CPTs are specifically designed to provide short duration high inrush while maintaining good voltage regulation, something that is critical in that application. You don't want the inrush of a motor starter coil to cause other things in the panel to drop out. A standard (cheap) potted distributioin transformer is not designed for that. So if you calculated that you need 2kVA from a CPT, you have better buy a 3kVA distribution transformer.
 

texie

Senior Member
Location
Fort Collins, Colorado
Occupation
Electrician, Contractor, Inspector
There is truth to Jraef's comment. Once again Jraef points out the finer points of motor control and all things related. We should all aspire to learn from him. Jraef, thanks for all your contributions!
 

templdl

Senior Member
Location
Wisconsin
Remember that a 480-240/120 transformer has a sengle winding secondary with a center tap (ct) and, yes, as such if you only need 120v for a single 120v circuit you will only have 1/2 of the kva on the transformer available.
As one of the other guys suggested get a transformer with a 120/240v secondary which has (2) 120v windings where X1-X2 is one winding and X3-X4 is the other. By simply connecting X1 and X3 together and X2 and X4 together you will be paralleling each 120v winding and have 120v available between the X1-X3 and X-2-X4 with the full KVA of the transformer.
 

Cow

Senior Member
Location
Eastern Oregon
Occupation
Electrician
There is truth to Jraef's comment. Once again Jraef points out the finer points of motor control and all things related. We should all aspire to learn from him. Jraef, thanks for all your contributions!

I agree, I learn a lot from Jraef's posts!:cool:

And I thought a transformer is a transformer is a transformer. Never would of guessed there was a significant difference.
 
Status