I know theres no 'code' issues here that I can think of, but I dont think this is common practice, at least I have not seen it done this way.
Theres this control cabinet (that controls 3 motors) that was not wired correctly, the 'run' indication lights are wired in parallel with each motors disco. Basically, you can turn off disco 1 and leave at least one other disco on (2 or 3) and turn the 'hand off auto' of motor 1 to the hand position and the run light will come on, showing that motor 1 is running, but in reality its not.
The controls are 120v (including the lights), which is normal, the motors run off of 3 phase 480. I suggested to a guy to correct this issue he just use some auxilary contacts on the each contactor and wire the indication lights off of them, so when that particular motor contactor is closed, the the lights will come on only at that time.
He wants to run '480 volt' to the indication lights off of the load side of the contactor (the t1, t2, t3 leads to the motor), basically just tapping off of them that way. He has to special order these '480' lights. Apparently he feels this will give 'true' indication. Would you wire it this way, or the way I suggested seeing that the 120 is already there from the transformer.???? 120 and below has always been for controls in my experience, including the lights.
Theres this control cabinet (that controls 3 motors) that was not wired correctly, the 'run' indication lights are wired in parallel with each motors disco. Basically, you can turn off disco 1 and leave at least one other disco on (2 or 3) and turn the 'hand off auto' of motor 1 to the hand position and the run light will come on, showing that motor 1 is running, but in reality its not.
The controls are 120v (including the lights), which is normal, the motors run off of 3 phase 480. I suggested to a guy to correct this issue he just use some auxilary contacts on the each contactor and wire the indication lights off of them, so when that particular motor contactor is closed, the the lights will come on only at that time.
He wants to run '480 volt' to the indication lights off of the load side of the contactor (the t1, t2, t3 leads to the motor), basically just tapping off of them that way. He has to special order these '480' lights. Apparently he feels this will give 'true' indication. Would you wire it this way, or the way I suggested seeing that the 120 is already there from the transformer.???? 120 and below has always been for controls in my experience, including the lights.