delectric123
Senior Member
- Location
- South Dakota
I am trying to integrate level control into an existing system. I didn't install the probes but the guy who did has tried to fine-tune them, even consulting the manufacturers with little luck. It has been working so-so for a couple years now.
Its a Schneider Electric Altivar 61 480-VAC 15 HP drive with for a pump that keeps a 50 gallon stainless steel cone shaped tank full on a separator that separates the solids from the water. The separator is about 15 ft. above the pump on a different floor. The separator uses a 480 VAC 3 hp motor controlled by a motor starter. The drive references a 4-20 mA 36" probe that's made by Delta Controls. There are two such setups side by side. That means two drives, two pumps, two separators with tanks, and two probes. Both are giving the same problem.
I've tried everything I can to get the tanks consistently full with water. I've tweaked the PID settings so the pump consistently accelerates and decelerates, but my problem is, the 4-20 mA reading is inconsistent. One day the tank is overflowing, the next day I check the level is about 4 in. different. Its probably best to talk to the manufacturers but maybe you guys can tell me something I don't know about 4-20 mA control.
These are $500 probes and I've done calibrated them correctly according to instructions. They're about 100 ft. away from the drives, the signal cables are 18 AWG twisted shielded in a separate conduit and with shield grounded at drive and probe housings are plastic so there's no grounding at water tank. The drives for both pumps are in a stainless steel enclosure right next to the 480 VAC Service Panel. The pumps are about 50 ft away from drives. I checked all the grounding and bonding and found no error. The conduit runs for the pumps are never even close to the signal conduit. The signal conduit runs in an isolated place crossing all line voltage conduits.
!00 % value at drive is 36" but drive never reads more than 30" to 32". A lot of times I've checked the probe output reads 100%, but the drive analog input only reads 17 mA. One thought, maybe the stainless steel tanks are goofing things up.
Its a Schneider Electric Altivar 61 480-VAC 15 HP drive with for a pump that keeps a 50 gallon stainless steel cone shaped tank full on a separator that separates the solids from the water. The separator is about 15 ft. above the pump on a different floor. The separator uses a 480 VAC 3 hp motor controlled by a motor starter. The drive references a 4-20 mA 36" probe that's made by Delta Controls. There are two such setups side by side. That means two drives, two pumps, two separators with tanks, and two probes. Both are giving the same problem.
I've tried everything I can to get the tanks consistently full with water. I've tweaked the PID settings so the pump consistently accelerates and decelerates, but my problem is, the 4-20 mA reading is inconsistent. One day the tank is overflowing, the next day I check the level is about 4 in. different. Its probably best to talk to the manufacturers but maybe you guys can tell me something I don't know about 4-20 mA control.
These are $500 probes and I've done calibrated them correctly according to instructions. They're about 100 ft. away from the drives, the signal cables are 18 AWG twisted shielded in a separate conduit and with shield grounded at drive and probe housings are plastic so there's no grounding at water tank. The drives for both pumps are in a stainless steel enclosure right next to the 480 VAC Service Panel. The pumps are about 50 ft away from drives. I checked all the grounding and bonding and found no error. The conduit runs for the pumps are never even close to the signal conduit. The signal conduit runs in an isolated place crossing all line voltage conduits.
!00 % value at drive is 36" but drive never reads more than 30" to 32". A lot of times I've checked the probe output reads 100%, but the drive analog input only reads 17 mA. One thought, maybe the stainless steel tanks are goofing things up.