I have a few question about a 120 volt 20 amp duplex receptacle circuit for a 620' tunnel.The customer is wanting one every 40'.
Question1. When calculating the voltage drop for wire size, can I calculate at the 80% of the 20 amp breaker?

Question2. Do I need to calculate to the last device? Or calculate the voltage drop for the first 300' and then the remainder 300'?

Question3. Do I calculate at 3% or 5%?

I was thinking the 3%, 20 amp at 620'. Given variables requires #1 wire.
Question4. Is this correct?

Given the result, we planned on #1 wire, set a jbox every 40', make a pigtail joint to #10, and whip into a single gang box for the receptacle.

Question5. Is this over kill?
 

Ingenieur

Senior Member
Location
Earth
better plan on a point load of 20 A at the last recept imo 3%'drop

0.03 x 120 = 2 x 620/1000 x 20 x R
R = 0.145 Ohm, you need R<0.145 from NEC table, steel cond, Cu
from table 1/0 = 0.13, #1 = 0.16
imo you could get by with the #1 at ~ 3.3% drop

imo pig tail can be #12
 

ActionDave

Chief Moderator
Staff member
Location
Durango, CO, 10 h 20 min from the winged horses.
Occupation
Licensed Electrician
Question5. Is this over kill?

The 3 and 5% stuff in the NEC is nothing more than a suggestion. The fact of the matter is voltage drop is load dependent and anything that works on 120V is made to tolerate voltage as low as 90V.

What's being powered up at these recepts every 40'? Hammer drills? Cell phone chargers? Sump pumps?
 

DSCOTTD

Member
Location
COCOA
The 3 and 5% stuff in the NEC is nothing more than a suggestion. The fact of the matter is voltage drop is load dependent and anything that works on 120V is made to tolerate voltage as low as 90V.

What's being powered up at these recepts every 40'? Hammer drills? Cell phone chargers? Sump pumps?

So basically you are saying if the receptacle may never get used, don't worry about it and pull #12.
 

DSCOTTD

Member
Location
COCOA
better plan on a point load of 20 A at the last recept imo 3%'drop

0.03 x 120 = 2 x 620/1000 x 20 x R
R = 0.145 Ohm, you need R<0.145 from NEC table, steel cond, Cu
from table 1/0 = 0.13, #1 = 0.16
imo you could get by with the #1 at ~ 3.3% drop

imo pig tail can be #12

Thank you for the reply.
 

winnie

Senior Member
Location
Springfield, MA, USA
Occupation
Electric motor research
I don't think that ActionDave is saying 'ignore voltage drop'. Rather he is saying that it is a design issue, not a code issue. You need your customer to define what you are using these receptacles for!

If the only reason is to supply low power loads, then you don't need to size for even 16A.

But say the customer expects to run some sort of largish motorized tool; even though this is nominally a 20A circuit, you may need to size it for 60-100A of starting current...but this transient requirement may be fine with a 10% drop,

You simply can't know without talking to the customer about what they want to plug in.

Depending on the desired loads, you can steer the customer to something that they can be happy with.

-Jon
 

ActionDave

Chief Moderator
Staff member
Location
Durango, CO, 10 h 20 min from the winged horses.
Occupation
Licensed Electrician
So basically you are saying if the receptacle may never get used, don't worry about it and pull #12.

That's not what I said at all. You asked "Is this overkill?" and I said there is no way to know that unless there is some notion of what the load is going to be.

I ran a 20A circuit about six hundred feet out to an electric gate opener. All that was being powered up was a trickle charger for a battery and a camera. I could have gotten away with 12AWG but went ahead and pulled 10AWG which was overkill for the loads being served.
 