Conversion of 20kA Short circuit current at 3sec to 1 sec?
SS_EE
Thailand
Engineer
Hi all,
Can anyone let me know how do we convert a short circuit current at 3 second to 1 second? I know we need to use I^2*t but I am not getting the right value as it must be higher at 1 second
Appreciate your help
Hi all,
Not sure what you mean by “convert” a short-circuit current. Can you clarify what you are trying to do?
what would be the short circuit current for the bus at 1 sec if it has a short circuit rating of 20kA for 3 second?
The steady state short-circuit current is 20-kA regardless of time or breaker settings. Short-circuit current magnitudes only vary in the first few cycles as it transitions from sub-transient to transient to the final steady state value. Your question doesn’t make sense. Are you trying to determine the magnitude of fault current that would correspond to a breaker trip time of 1 sec? If so, it depends on the breaker make/model and settings if it’s adjustable. I suggest referencing the published TCC or back-solving if you know the TCC equation.
20 KA FOR 3 SECONDS, is the. main bus short circuit withstand rating. and. is. fixed. as. the design. Min feeders have a short circuit withstand rating of 1 second when properly sized for the available short circuit. Look up BUSSMANN.
You can not convert it. You do not have the proper information in order to construct a time current damage curve.
Your bussing can tolerate a maximum of 20kA for a maximum of 3secs. Your job is to provide a protective device whose curve falls to the left of these two values.
See IEC 60865-1 Short-circuit currents_Calculation of effects
If you know Ithr for 1 sec you may calculate for 3 seconds since Ith<=Ithr and Tk>Tkr. Other way it is not permitted.