Conversion table for computed load calcs
I have been told that there is a conversion table for load calcs. I have a twin pack heat pump system and I am having trouble with the proper percentages to use to fill out the remainder of the calcs. If the unit is a 20kw what is the correct formula to use for conversion?
Re: Conversion table for computed load calcs
I need to convert the 20kw to total amps used for for electrical usage, i.e.
Two seperate heat pump twim packs
One 5 ton unit that is 20kw with a
20kw heating element
One three ton unit that is 15kw with a
7.2kw heating element
total is 62000 watts
Is the conversion 62000 X 65% to
calculate the correct percentage of power
usage?
russ
Burbank IL
220.30(C) Tells you what percentage to use depending on the equipment type, and the controller functions.
Russ
[ April 18, 2003, 10:14 PM: Message edited by: russ ]