There is no direct conversion because of different SEER ratings. But for estimating I use 8 amps per ton single phase and 6 amps per ton 3 phase. These numbers will get you close enough up to 5 tons. But for actual wire sizes I wait for name plate data. I sometimes get the HVAC contractor fax me equipment data on their letterhead to make them responsible.
 
We need to be careful about if we are talking electrical "wattage", or heating/cooling wattage.

It is possible to do a mathmatic conversion from tons to watts, but that isn't the same as the electrical input watts (or amps or KVA).

The other thread had a couple of responses that seemed to be refering to heating/cooing wattage.
 
How do you convert A/C tonage to wattage for single phase and 3-phase load calculations?

You can ball park it but in the end you need the info from the unit. There are major differences in efficiency and design.


If I told you a car has a 200 HP motor could you tell me the MPG?
 