Assuming the original was supplied with 50 amp conductors - splice on smaller conductors with an approved splicing method for the conductors utilized, chances are the new device will not accept the larger conductor that is present. And as mentioned reduce overcurrent protection to the correct size. You may have to reduce conductor size at the overcurrent device also, as many 15 amp devices will not accept conductors larger then 10AWG.I have a NEMA 10 250V50A receptacle and I need to change this to a NEMA 6 15A Receptacle.
How would I go about doing this? Novice here, so please keep it some what simple.
My best two answers would be, (1) You don't. Instead you throw this one out and buy the one you need, and (2) Why should you want to do that?
Welcome to the forum.
Assuming the original was supplied with 50 amp conductors - splice on smaller conductors with an approved splicing method for the conductors utilized, chances are the new device will not accept the larger conductor that is present. And as mentioned reduce overcurrent protection to the correct size. You may have to reduce conductor size at the overcurrent device also, as many 15 amp devices will not accept conductors larger then 10AWG.
This helps a lot. My problem is going from a 3 phase receptacle to a single.
The 10-50 receptacle wasn't ever intended to be used for three phase in the first place.
That said you would still likely have to reconnect leads to the proper source for what you need.
How did they get an equipment grounding conductor to prior used equipment?
Yes, it is the commonly used receptacle for a household electric range (three wire supply).I might have this wrong, but isn't a NEMA 10 50A a L1/L2/Neutral?
This helps a lot. My problem is going from a 3 phase receptacle to a single.
My recommendation is that this is not something a novice should take care of. It requires removing a 50A-2P circuit breaker from the panel and installing a 15A-2P in its place, and either correctly re-color-coding the wiring at both ends or replacing the run with #14/2 NM-B (which is what I would do, assuming it's a residence). And also as someone mentioned, moving the neutral to the ground bus.
You should hire an electrician for this work.