electrofelon
- Cherry Valley NY, Seattle, WA
- Electrician
I have a 120/240 high leg delta service serving a building that has 5 accounts/meters. Three dwellings, a deli, and a club. The club's service is three phase but I think all the others are single phase. The clubs disconnect has all three phases run to it, but no fuse on the B phase and no wire run from the load side of the disco to the 200 amp panel. The only line to line load in the club is a walk in cooler. The client wants to add a grow room fed off the clubs panel. I did a load measurement while the club was up and running and its going to be close with this grow room added. Actually it will be fine most of the time but now and then when they have a real big act, they run extra lights and sound and that's what I am worried about. This got me thinking - probably more of an academic questions at this point but: What if I had the utility change the service to a 120/208Y? Any implications/ramifications that I am missing? Here is what I have come up with:
1. The club's meter and maybe socket would need to be changed, not sure about the other 4 single phase, depends on their meters I guess...?
2. Obviously lower wattage for ranges and water heaters - no biggie. Maybe would want to look at equipment in the deli to see if ok with 208
3. Un-identify the high leg
That's all I have, am i missing something or would it actually pretty much turn key after the utility does their end?
The theory is that this would free up space in the panel and things could be balanced out nicely.