I did a service calculation for a friend using Mike's Residential Calculation spreadsheet.
The power company came back and said the calc must be done on their sheet. They use KW for the connected loads. It's been a bunch of years since I did much in conversions.
If I have a 1,200 VA load for heat is that the same as 1.2 KW? Or do I need to take a power factor into consideration? If so, what factor?
It's for a residential, single phase 120/240 volt 200 amp service.
This is the sheet they want me to use:
https://lge-ku.com/sites/default/files/documents/load_data_sheet.pdf
I'm using this calc sheet from Mike:
http://www.mikeholt.com/documents/calculations/formulas/ResidentialLoadCalculations.xls
Thanks for all the help you guys give me and everyone else.