line_noise
Member
Job has a couple of 480 delta-240 delta transformers we are replacing, each serving a box with 3 fuse holders for transformer secondary OCPD, and taps to fused switches to serve 3 phase motor loads. Pretty sure it was all ungrounded, as I didn't find any evidence of a grounding electrode or bonding jumper, and the color codes are Black/Red/Blue. Loads are three phase motors. Lighting, receptacles etc. in the plant are fed from different transformers.
Owner has preference for solid grounding, so we are planning on changing to corner grounding and installing new panelboards to replace the old switches and gutters. We made sure the breakers have correct voltage ratings. So we are good there.
Only thing I can't get around, is Article 200 requiring that the grounded conductor be white. We can tape the bigger ones, but tracing and replacing all of the smaller ones will be a pain. Lots of stuff is 60 year old cloth wiring, and we'd have to repull all the circuits, which we weren't planning on, and is going to require more downtime.
Can anyone comment on the safety issue on a 3-wire delta system of having white grounded conductor in 200.6? We'd like to just ground the B phase and leave it red, but there must be some reason code says what it does. I guess if the inspector won't allow it, we can pull the bonding jumper and leave it ungrounded.
Any insight would be appreciated, I don't run across delta secondary systems often.
Owner has preference for solid grounding, so we are planning on changing to corner grounding and installing new panelboards to replace the old switches and gutters. We made sure the breakers have correct voltage ratings. So we are good there.
Only thing I can't get around, is Article 200 requiring that the grounded conductor be white. We can tape the bigger ones, but tracing and replacing all of the smaller ones will be a pain. Lots of stuff is 60 year old cloth wiring, and we'd have to repull all the circuits, which we weren't planning on, and is going to require more downtime.
Can anyone comment on the safety issue on a 3-wire delta system of having white grounded conductor in 200.6? We'd like to just ground the B phase and leave it red, but there must be some reason code says what it does. I guess if the inspector won't allow it, we can pull the bonding jumper and leave it ungrounded.
Any insight would be appreciated, I don't run across delta secondary systems often.