Converting Transformer Classifications Old to New
dnem
Ohio
The problem is that Im getting conflicting info
This site says
http://www.hammondpowersolutions.com/faq/what-is-meant-by-class-in-insulation/
old class A is new class 105
old class B is new class 150 or 130
old class F is new class 180
old class H is new class 220
This site says
http://www.electricalengineeringtoolbox.com/2014/08/nema-insulation-classes-for-transformers.html
old class B is new class 130
old class F is new class 155
old class H is new class 180
old class R is new class 220
Who is correct.?
dnem
Ohio
In addition, I'm referencing this ATP book that refers to "class 150" repeatedly. And Im seeing "class 155" spoken about in the NEC 450.21(B)X1+X2. Does this NEC reference prove that all references to class 150 are wrong.? Why would somebody makeup a class 150.?
I wish I could access the NEMA website. They apparently want money just to see the simplest thing. I dont see how I can access the answer to even a basic question without paying them for a subscription.
dnem
Ohio
Schneider / Square D is a pretty reliable source but so is NFPA. Since NEC 450.21(B)X1+X2 states that there is a class 155, are both sources right.? Is there both a class 150 and a class 155.?
Smart $
Esteemed Member
Ohio
I don't believe there is a "standard" 155. I believe the 155 value was chosen so it would be higher than 150, but much closer to 150 than 180 just in case some manufacturer published a non-standard in-between rating.