alblock
Member
- Location
- NC, TN, SC
- Occupation
- Industrial Electrician
A supervisor came over the radio saying a conveyor was shocking people. Its a portable metal conveyor with rubber wheels. It has a 3p 480v gear motor that's powered by a vfd. The drive gets power through a L16-20 locking plug. When the motor was running i measured 160v from the conveyor and any metal object that was grounded. The conveyor being on rubber wheels wasn't grounded. I found the ground wire going to the drive was pulled out from the terminal. I connected the ground wire and the voltage went away. I didn't find any nicked wires or lose connections. I measured the motor phase to phase resistance and all were the same. I used a fluke megger and all phases read 550 mega ohms at 500v to the motor frame. The factory installed bond between the drive and the motor was good. I don't fully understand why there was a voltage with the motor checking good. I thought an ungrounded conductor would have to be touching something to cause this. Was this because the motor was on a vfd? Would this happen to any motor that loses ground? Thanks