I have never been asked to do a coordination study on my PLC Control panel.
I'm using various amperage of the same Allen Bradley Breakers
1489-A1D020 - 2 Amp
1489-A1D030 - 3 Amp
1489-A1D050 - 5 Amp
1489-A1D200 - 20 Amp
These breakers feed power to I/O module,Power Supplies, and various transmitters in the field (Ultra Sonics, Flow Meters, Gas Analyzer).
The Engineer reviewing my Panel Drawings is requesting a coordination study for the breakers and main breaker in my panel that gets power from the distribution panel.
I would believe if a fault (Line-Ground) were to occur the branch circuit breaker that is experiencing the fault would trip first. None of these breakers have adjustable trip curves.
My response for the my Main breaker to the distribution panel would be for the Arc Flash firm who is doing all the calculation on new equipment.
Do these response have a case?
I'm using various amperage of the same Allen Bradley Breakers
1489-A1D020 - 2 Amp
1489-A1D030 - 3 Amp
1489-A1D050 - 5 Amp
1489-A1D200 - 20 Amp
These breakers feed power to I/O module,Power Supplies, and various transmitters in the field (Ultra Sonics, Flow Meters, Gas Analyzer).
The Engineer reviewing my Panel Drawings is requesting a coordination study for the breakers and main breaker in my panel that gets power from the distribution panel.
I would believe if a fault (Line-Ground) were to occur the branch circuit breaker that is experiencing the fault would trip first. None of these breakers have adjustable trip curves.
My response for the my Main breaker to the distribution panel would be for the Arc Flash firm who is doing all the calculation on new equipment.
Do these response have a case?