Cooking equipment demand factors

Status
Not open for further replies.
Assuming this is a test question, have you looked at 220.55 & 220.61 ??
We prefer you make an attempt at the answer rather than just answering it for you.
 
35 apartments, each has a 12kw range 120/240v single phase. What is the neutral demand for the service?

whats does the 120/240 stand for? How do you solve this problem?


120/240 means the unit is a 240 volt appliance with a 120 volt load (light or fan). Thus you would need 2 hot conductors plus a neutral.
 