The issue of the correct overcurrent device for single fed cooking appliances had bugged me forever an I have not been able to get a clear answer. I will tell you what I currently do and why and perhaps y'all can approve it or tall me what I am doing wrong. I will be content either way.
I go to article 240 and Table 240.3 sends me to 422. Section 422.10(A) refers me to Table 220.55 and 210.19(A)(3).
Table 229.55 tells me to take 80% of the nameplate for cooking equipment under 8 3/4 kw.
210.19(A)(3) tells me that under 8 3/4 kw they shall have an ampacity not less than the branch circuit and not less than the load to be served. Since the branch circuit is the kw rating at 80% and the load to be served is the actual kw rating, I would assume then that the overcurrent device would be the higher of the two or the kw eating at 100%.
Someone was telling me to use 125% but this seems unreasonable since cooking equipment universally gets the branch circuit derated.
I would appreciate input.
I go to article 240 and Table 240.3 sends me to 422. Section 422.10(A) refers me to Table 220.55 and 210.19(A)(3).
Table 229.55 tells me to take 80% of the nameplate for cooking equipment under 8 3/4 kw.
210.19(A)(3) tells me that under 8 3/4 kw they shall have an ampacity not less than the branch circuit and not less than the load to be served. Since the branch circuit is the kw rating at 80% and the load to be served is the actual kw rating, I would assume then that the overcurrent device would be the higher of the two or the kw eating at 100%.
Someone was telling me to use 125% but this seems unreasonable since cooking equipment universally gets the branch circuit derated.
I would appreciate input.