ok, thanks.If you have gas and electricity, they both must shut down.
I can't remember which code it was in, maybe the fuel gas code or building code... it says if the fire suppression system is triggered, and it shuts down the master gas control valve, you don't need to shunt the appliances beneath a hood. Is this right, wrong?
So for example, if you have a gas range... that's not required to shut down electrically?Electronic control circuits aren’t required to be shunted for gas appliances.
So for example, if you have a gas range... that's not required to shut down electrically?
10.4.1 Upon actuation of any fire-extinguishing system for a cooking operation, all sources of fuel and electric power that produce heat to all equipment protected by the system shall automatically shut off.