Am I right on this? I got a 4 kw oven and 7.6kw cooktop. 240v. So total is 11.6kw. Column C say 8 percent derate. After I derate the circuit it's 44.46 amps. We can put this on the old 50amp range wire.
 
For some reason this table is hard for people to understand. Col A and B are percent but Col C is KW. There are some many factors to look at but in your case Note 4 comes into play so you consider the 2 units as a single unit and then use Col C
 