Had an emergency service call on Sunday for a cooktop that had quit working. Determined that a faulty connection (possible overload) was the problem. Wirenut on the black was melted and there were obvious smells of burning. Remade the connections and it worked. However nameplate of the cooktop was 7.5kw at 240 and the branch circuit was #10 NM-B. That is a 31.25 amp load and was verified by my meter. All eyes on and it was 31.5 amps. So I’m writing up the invoice citing code 210.19(A)3 and suggesting upsizing the wire to meet code and prevent fires etc.
However the #10 showed no real sign of overheating. So question is was the overload really the culprit or was it just a bad connection?
However the #10 showed no real sign of overheating. So question is was the overload really the culprit or was it just a bad connection?