Is there a code requirement for the outdoor compresser and the indoor Fan coil being on seperate breakers.

I have a homemade control panel tht has a Main breaker that feeds a contactor with overloads for the inside fan unit and also parelels off the load side and feeds a breaker for the outdoor unit that has no contactor.

I'm used to seeing a main that feeds 2 breakers, 1 for the inside unit and 2 for the outdoor unit in the control panel. Each having its on contactors and overloads.

Does anyone know if this violates any codes.

Also I was checking the thermal overload and it would only open if you held the test butten in, if you let it go the contactor would close again. Acting like a momemtary switch. Most overloads I've tested in the past you can test it and will open and it wont close until you hit the reset button. This unit does have a reset button. Does anyone know if theres an overload that works like this.
 
Is there a code requirement for the outdoor compresser and the indoor Fan coil being on seperate breakers.

~
Does anyone know if this violates any codes.
Depends.... Most are seperate equipment and the OCP sized and limited to each - but due to size of the unit - the limits of the OCP size may not be able to handle the combined load. If that makes any sense? But some smaller units - the OCP may be able to handle both, and even control the other "through" the first by contactors at the compressor location.
 
Also I was checking the thermal overload and it would only open if you held the test butten in, if you let it go the contactor would close again. Acting like a momemtary switch. Most overloads I've tested in the past you can test it and will open and it wont close until you hit the reset button. This unit does have a reset button. Does anyone know if theres an overload that works like this.

Most IEC overloads and some NEMA electronic overloads have a hand/auto reset selector. The one you are questioning is probably set for automatic reset function.
 