Here's the scenario:
Trouble call for 4 lights not working in "frozen pizza " cooler.
Cooler in question is Zero Zone 5-door frozen food retail show cooler. There are three 2-lamp F40 T8 ballasts.
For troubleshooting, all the heat trace in the five doors are unplugged.
When the ballast leads are loose from the line, the line reads 120V (116V).
When any of the three ballast loads are tied to the line, the line drops to 80V.
By chance, the cooler cycled into defrost and the circulating fan quit running. Coincidentally, all six T8 tubes come on full bright. When defrost cycle ends, fan comes on and lights go dim again. Two additional cooler cases share this circuit but are working OK. Light circuit is pulling around 3 amps while the middle cases ballast are at 80V.
Why is this happening?
How is this fan circuit affecting the light circuit? I assumed the heat trace, lights and fan were all on the same circuit, but I don't know for sure.
Trouble call for 4 lights not working in "frozen pizza " cooler.
Cooler in question is Zero Zone 5-door frozen food retail show cooler. There are three 2-lamp F40 T8 ballasts.
For troubleshooting, all the heat trace in the five doors are unplugged.
When the ballast leads are loose from the line, the line reads 120V (116V).
When any of the three ballast loads are tied to the line, the line drops to 80V.
By chance, the cooler cycled into defrost and the circulating fan quit running. Coincidentally, all six T8 tubes come on full bright. When defrost cycle ends, fan comes on and lights go dim again. Two additional cooler cases share this circuit but are working OK. Light circuit is pulling around 3 amps while the middle cases ballast are at 80V.
Why is this happening?
How is this fan circuit affecting the light circuit? I assumed the heat trace, lights and fan were all on the same circuit, but I don't know for sure.