I have a customer who insists that a cooling tower fan on a variable speed drive falls under the classification of a continous rated motor being used for varying duty service as defined in Table 430.22(E) in the 2005 NEC.
I believe that the statement under this table:
"Note: Any motor application shall be considered as continuous duty unless the nature of the apparatus it drives is such that the motor will not operate continuously with load under any condition of use."
makes it pretty clear that something like an automatically controlled fan motor is not what the writers had in mind when they are talking about varying duty. Obviously the fan motor on a tower will operate continuously with load under most conditions of use. In fact, that is the main reason for using a variable speed drive on the tower - to eliminate cycling and the temperature swings it creates and force the motor to operate continuously, ableit at reduced speed.
He also made the following statement to me:
"The wiring, contactors, terminal blocks from the VSD output to the motor need to be rated for 200% of the motor FLA. This is because of the standing wave the drive can generate in the wiring per NEC code for variable duty running of the motor."
I'm not an EE. Is this what the code is about? "Standing waves"?
I believe that the statement under this table:
"Note: Any motor application shall be considered as continuous duty unless the nature of the apparatus it drives is such that the motor will not operate continuously with load under any condition of use."
makes it pretty clear that something like an automatically controlled fan motor is not what the writers had in mind when they are talking about varying duty. Obviously the fan motor on a tower will operate continuously with load under most conditions of use. In fact, that is the main reason for using a variable speed drive on the tower - to eliminate cycling and the temperature swings it creates and force the motor to operate continuously, ableit at reduced speed.
He also made the following statement to me:
"The wiring, contactors, terminal blocks from the VSD output to the motor need to be rated for 200% of the motor FLA. This is because of the standing wave the drive can generate in the wiring per NEC code for variable duty running of the motor."
I'm not an EE. Is this what the code is about? "Standing waves"?