cooling tower

Status
Not open for further replies.

m2oliva

Member
Can you size the branch conducter and circuit breaker by just knowing the full load inrush current of a temp cooling tower.Iam told the full load inrush current is 64 amps.The company that supplied the unit didnt know the min cir amp. or the max fuse size .
 
Re: cooling tower

no, those devices need to be sized based upon the FLA and min Ckt amps of the tower. This information should be available on the unit or by the manuf.
 